Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
Assuming a separately derived system transformer I would actually say the answer could potentially be a NO because NEC typically allows the system bonding jumper (connection between transformer secondary windings mid/ neutral point and ground only at ONE location to avoid objectionable current or a parallel neutral current path.On a 480/277 400 amp 3 phase service.
Do you need to bond the neutral to ground inside the current transformer box?
The neutral bar only has space for one wire.
This bond could technically be in the transformer if located outdoors away from the first point of disconnect for a YES to your question and not bond the neutral grounded conductor to the first point of disconnect neutral and ground buss as traditionally done
Or a NO if the transformer is located indoors adjacent to the first point of disconnect panel, where you would bond the neutral bus and ground buss but according to code not at two locations if objectionable current can result
In older systems pre 1996 where a neutral servers also as the supply side bonding jumper I think it’s allowed to have this bonding at both the first point of disconnect and transformer