Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
Another member posted a question on another post regarding what size wire to use for a 4,000’ foot run. The question was worded as:
Just wondering what size wire do i need if my run is 4000 feet at 480 from my switch wanting to step it up to 7200 an then from 7200 down again to 208/120 what size wire will i need. [to a 3 phase 400i ampere service]
When trying to help this guy out on figuring the proper size wire for the 4,000 foot span I first determined the size of the downstream stream transformer at
Secondary feeding the 400 ampere service
208E x 400i x 1.732 = 144.1 kVA transformer
Primary side amperes which would be seen on the 4,000 ft run = 144,102 VA / 7,200 VA x 1.732 = 11.555 i amperes
Now that the full load amperes on the 4,000 foot run is known between transformers we can calculate voltage drop and minimum wire size.
However when I use either one of two equations permitted with one using the resistance values for wires in NEC chapter 9 Table 8, they never seem to result in consistent answers? Why
For example, first determine max 2% voltage drop at feeder with 7,200 volts. 7,200 volts x 0.02 = 144 volts dropped max
Calculation method #1
Vd = 1.732 x K x I x D / CM
144 = 1.732 x 12.9 x 11.555i x 4,000’ / CM
Solve for CM (wire size in circular mill) = 7,171.42 cm
Match 7,171 circular mills to wire size chapter 9 Table 8 =
A #10 AWG wire with 144 volts dropped max
Calculation method # 2
I X R
VD = dc resistance (Ch 9 Table 8) x i x 1.732 x distance / 1,000
1.21 x 11.55i x 1.732 x 4000’ / 1,000 = 96 volts dropped
144 volts dropped in first equation does not equal 96 volts dropped in second equation but both are NEC acceptable methods. Both equations never result in the same results so how would you handle this during an NEC journeyman’s test?
I X R