Coming out the bottom of an exterior surface mount panel with RNC Sch 80, to LB (nm) through raised foundation, use remaining length of Sch 80 under house (exiting LB), then direct transition to about 4ft. of LFNC to come up inside a wall to terminate / connect to a metal box / outlet.
Couple of dumb questions:
I don’t use pvc that much anymore so I’m a little fuzzy on temp ratings… when the mfg says their RNC is rated for use with 90C conductors are they saying the pipe is rated at 90C ambient or just that it’s fine to install 90C conductors as long as I rate the conductors at 75C etc. or whatever not exceeding conduit’s ambient? (I realize the LFNC is only rated for 80C btw). Or is there a calc where you also need to add conductor current temp + conduit ambient? I remember it as you couldn't install RNC where the ambient was in excess of 50°C, but wondered if there were other grades now or new specs (?)
When 356.10 yaps about lengths of LFNC not to exceed 6ft ... am I skirting any intentions by mechanically transitioning from the RNC directly to the short 4ft. piece of LFNC ? I.e. do they just expect LFNC to be only be used as a whip from disco/enclosure etc to equipment?
On an aside - I was reading some of Carlon’s specification lit where they say- “Conduit, fittings & cement shall be produced by the same mfg to assure system integrity.” Makes sense, but is there anything in the code or has anyone had an inspector hold them to this? (just curious, not really important).