synchro
 - Chicago, IL
 - EE
In the diagram you attached, the CT's will only measure the current going from the inverters to the grid. But it would not include the current supplied to the loads by the inverter's load output terminals, or supplied by the grid directly to the loads in bypass mode. Wouldn't you want the CT's to measure the total net current flowing to or from the grid?
I don't see the need. The inverters know how much current they are outputting, and they can add or subtract what they measure at the CTs to determine what is being consumed by the loads. The diagram is how most manufacturers do it.
On page 55 of the Sol-Ark-15K manual at the link below, they show the CT's placed right after the meter.
This diagram has a bypass mode like in the OP's diagram where the loads can be connected directly to the grid and not to any terminals on the inverters. And so in bypass mode, I believe the inverters would not know what the net current through the connection to the grid would be because of a lack of information about the load current. But I could be wrong.
https://www.solar-electric.com/lib/wind-sun/Sol-Ark-15K-Manual.pdf