dvcraven0522!
Member
- Location
- St. Louis
- Occupation
- Electrical Design
I have a pull box mounted to a CMU wall to feed (2) MCC's at 800 ea. with 3#600kcmil with (8) 4" conduits. Four of the conduits are spare/
I took 6x4"+4+4+4 = 36" for height and width of the box. My question is how to figure the depth. I am thinking I might be able to use the wire bending space on table 312.6(A). For 600kcmil with 3 terminations per phase for a 12"depth.

I took 6x4"+4+4+4 = 36" for height and width of the box. My question is how to figure the depth. I am thinking I might be able to use the wire bending space on table 312.6(A). For 600kcmil with 3 terminations per phase for a 12"depth.