With the four remaining players we have today Square D, Eaton, Siemens, and GE and the product lines those four have acquired in the past 40 years, when one trips it won't have enough force to pull others with handles tied to it into the off position.Is it possible if one does trip and the other does not with a handle tie on it?
However in order to reset the one that has tripped you likely will end up turning the non tripped one(s) off in the process.
There may be some old obsolete breakers out there that can do so.