winnie
- Springfield, MA, USA
- Electric motor research
The intent of 310.15(B)(5)(c) is to deal with the situation of nonlinear loads which draw harmonic currents which result in current flowing on the neutral conductor even when phase conductor currents are balanced. Clearly this issue only presents if the non-linear loads are connected line to neutral.
However the text of the code is:
Question: Consider a 480/277V 4-wire feeder to a panel. The panel supplies 300A worth of VFDs and 50A worth of L-N 277V resistive loads. By the wording of the code is the neutral of that feeder counted as a current carrying conductor?
As I understand the physics of the situation, there will be no harmonic generating loads connected to the neutral and no issue of harmonics on the neutral. So it shouldn't count as a CCC, and IMHO common sense would say not to worry about the issue.
But the majority of the load on the feeder is from the nonlinear input rectifiers of the VFDs. So by the wording of the code I think the neutral must be counted as a CCC. I don't see anything in the wording of the code that specifies nonlinear L-N loads only.
Thanks
Jonathan
(c) On a 4-wire, 3-phase wye circuit where the major
portion of the load consists of nonlinear loads, harmonic
currents are present in the neutral conductor; the neutral
conductor shall therefore be considered a current-carrying
conductor
Thanks
Jonathan