Ok, interesting and thanks. What is used more often when having to use compression fittings? Would they allow you to use one with set screws if compression fitting were specified?Good question so others can learn. Some LBs have SS on hub, others have FM threads to use with EMT connector,
But IDK about cost, I used and see mostly the FM thread type
Some will say a technical violation but that's how you would do it if compression EMT fittings are required.If the LB had female threads would a standard compression connector like this be used?
How have you done it most jobs? Set screw LB or comp connector?Some will say a technical violation but that's how you would do it if compression EMT fittings are required.
Yup. We use them anyway. No one really cares if you screw a compression connector into a conduit body. We always use set screw fittings unless forced to use compression.Connector not listed to be used with LB?
LB's exist that are basically combos; they have threads for use with RMC and threaded fittings (stupid listing issues be damned), as well as set screws that allow you to just install it on the end of a piece of EMT. Home Depot is selling these "combo" style LBs, probably so they can stock fewer part numbers.How have you done it most jobs? Set screw LB or comp connector?
Why a volation? Connector not listed to be used with LB?
So you've used LB's with set screw on a EMT conduit run with compression couplings?Yup. We use them anyway. No one really cares if you screw a compression connector into a conduit body. We always use set screw fittings unless forced to use compression.
No, we've used a compression EMT connector screwed into the LB even they it's not allowed (don't tell).So you've used LB's with set screw on a EMT conduit run with compression couplings?
While used everyday without issue, it is a listing and evaluation issue. The following is from the UL Guide Information for "Conduit Fittings (DWTT)".How have you done it most jobs? Set screw LB or comp connector?
Why a volation? Connector not listed to be used with LB?
Note that the second two statements are in conflict with the first statement.Fittings with internal female threads (e.g., hubs, conduit bodies, couplings) have only been investigated for use with threaded rigid conduit.
Male fittings not provided with a locknut, intended for securement to a threaded hub, are marked on the smallest unit shipping carton, "For securement to a threaded hub only," or the equivalent.
Male fittings provided with a locknut, also intended for securement to boxes with threaded entries, hubs or fittings with internal female threads (e.g., conduit bodies, couplings), are marked on the smallest unit shipping carton, "For securement to a threaded hub," or the equivalent.
Same with about 98% of the LFMC conduit connectors that I have installed...and expect that is true for every electrical that has worked industrial projects.No, we've used a compression EMT connector screwed into the LB even they it's not allowed (don't tell).![]()
Not really. The distinction is with respect to who does the investigation.Note that the second two statements are in conflict with the first statement.
What type of fitting o you use with LFMC? SHouldn't it be a malleable fitting?Same with about 98% of the LFMC conduit connectors that I have installed...and expect that is true for every electrical that has worked industrial projects.
Typically you change over from a rigid raceway with a threaded coupling.What type of fitting o you use with LFMC? SHouldn't it be a malleable fitting?
What is you don't? e.g. LFMC from disconnect to motor.Typically you change over from a rigid raceway with a threaded coupling.
It's not unsafe. It's an on-paper-only listing issue.This entire argument is silly and should be resolved. This is a common installation practice and I've never seen any real world data to say that it's unsafe.