rosslet
- Ohio, United States
- Automation/Controls Engineer
Short version: on a single-phase 480VAC to 240Volt center tap transformer, if each of the 120VAC circuits has 50Amps being fed, how much current returns to the transformer on the center tap neutral wire? IE do I need a neutral wire capable of 100A feed or 50A? Assuming all power wires are sufficiently sized etc.
Long version: I have a client that wanted a 240Volt water heater added last minute to a control panel with 480VAC in it so we specified a floor mounted transformer from 480V to 240V (single-phase). This is an industrial application. At the last moment, again, it was decided to bring 120VAC back to the panel for possible future use. So we plan to ground and bring the center tap on the 240V Secondary side back in case they wanted to ever add 120V loads to this panel. So to be clear, we're only adding a single 240VAC load, no 120VAC loads.
I found article 220 (quoted at the end) code seems to imply you must size it at the time of adding loads, which would imply this specific aspect has no affect on me as their are no loads yet or possible ever. So in that case, the size of the neutral need only be as large as the grounding wire (which is somewhere else in code I don't recall off hand) and the ground was 6AWG in this case. The original plan was simply to have three terminal block busses containing the two taps and the neutral. Someone wants to add anything, they wire to these terminal blocks, and balance between the two taps as they add loads.
But it got me thinking, I don't want to leave this circuit easy to screw up for the next guy, so I added a circuit breaker upstream of each power terminal block bus. The idea is, someone will have to bump up this breaker if they want more capacity and in theory they need to take a peak at the capacity as opposed to people just blindly slapping more load on until the larger phase wires are fine but the neutral smokes or something.
So, the 6AWG neutral circuit has components that can take at least 50 Amps, therefore I originally put a 50A breaker to each of the two power terminal block busses.
Which brings us to our question, if both taps are running 50 Amps, is the return load on the neutral to the transformer 50A or 100A?
I got nervous and bumped the breakers down to 20A, which ensures this issues won't be possible, but I cannot for the life of me land on this one and would love some input! Thanks for reading!
NFPA 70 220.61
(A) Basic Calculation
The feeder or service neutral load shall be the maximum unbalance of the load determined by this article. The maximum unbalanced load shall be the maximum net calculated load between the neutral conductor and any one ungrounded conductor.
Exception: For 3-wire, 2-phase or 5-wire, 2-phase systems, the maximum unbalanced load shall be the maximum net calculated load between the neutral conductor and any one ungrounded conductor multiplied by 140 percent.
oh and little bonus question, does anyone know how one is supposed to refer to the different taps on these split phase systems? I believe they're not two phases in the same way say two of three phases in a 480V delta system. So if they're not really two "phases" what are we supposed to call them? I've started calling them top and bottom tap.
Wikipedia's split phase electric power says this on it which makes sense, but doesn't answer to me what is a sensible way to refer to them.
"Since the two phasors do not define a unique direction of rotation for a revolving magnetic field, a split single-phase is not a two-phase system."
NFPA 70 220.61