It is the GFCI function of the breaker that is apparently tripping it, doesn't mean there is an actual ground fault occurring.
Some "noise" on the line even if unloaded causes GFCI's to trip, even if not originating from the protected portion of the circuit.
I once had a wall switch type occupancy sensor left over from a job, thought I would put it in the bathroom in my shop. Right away it kept causing a GFCI receptacle nearby (think on same circuit but said light was not on load side of the GFCI) to trip every time the light was on. Never did figure out why as I put regular switch back in right away figuring it don't like to play well with the GFCI. That has been like 15 years ago when I did that.
GFCI's don't like inductive kick back or other transients either. sometimes even when on the supply side of the circuit. Name brand ones are better at handling it but still sometimes trip when a big enough surge hits them, like during thunderstorms or even when POCO is having issues and maybe a circuit recloser is cycling or other switching activity causes transients on the line.
If all your effected GFCI's are tripping at same time maybe it would be easier to figure out some event that is occurring when they trip.