brycenesbitt
- United States
I'm seeking help understanding the electrical concern identified by a large West Coast power company:
"Transformer's thermal rating of 35 kVA (summer coastal region); however, due to the almost 300 ft. of secondary conductor to the interconnection customer, this may result in excessive voltage-rise. Therefore, it is proposed to remove and replace the existing transformer, and up to 200 ft. of secondary conductor, to mitigate this. Estimating to confirm the mitigation(s) needed during the implementation phase. The transformer and secondary conductor replacements are considered Distribution Upgrades... updates will take 6 months to 12 months.... Any facilities (transformer or secondary cables) that are found to be dedicated to the customer and that would need to be replaced would be at the cost responsibility of the customer ."
The early review of the project showed no problem:
the supposedly final signoff prior to interconnection generated the above.
The project added a 57.1 kW nameplate microinverter solar generating facility to an existing building with two 100A meter mains.
The same poco transformer feeds six other properties at least, on two poles between lot lines.
I'm trying to understand how adding solar generation impacts the voltage on the transformer.
The southwire drop calculator shows:
Engineering Information 4/0 Aluminum
0.1100 Ohms Resistance (Ohms per 1000 feet)
0.0410 Ohms Reactance (Ohms per 1000 feet)
0.9 Power Factor
2.92% Voltage Drop
I see https://mcelectrical.com.au/solar-voltage-rise-explained/
But am looking to understand exactly which voltage the poco is worried about above.
0.9 Power Factor
2.92% Voltage Drop