what size and deep
timmermeier
alton il
electrician
What size and deep and wire do i need for a ground plate , for 200 amp service. ( home ) ?/////////////////////////////////////////////////////////////////////////////////////////////////////////////////////
here you go
(7) Plate Electrodes. Each plate electrode shall expose not
less than 0.186 m2 (2 ft2) of surface to exterior soil. Electrodes
of bare or electrically conductive coated iron or steel plates
shall be at least 6.4 mm (1∕4 in.) in thickness. Solid, uncoated
electrodes of nonferrous metal shall be at least 1.5 mm
(0.06 in.) in thickness.
(H) Plate Electrode. Plate electrodes shall be installed not
less than 750 mm (30 in.) below the surface of the earth.
here you go
1.5 mm is less than 1/16 of a inch . pretty thin ?