FIRE PUMP CONTROLLER WILL REQUIRED A NEUTRAL FROM GENERATOR FEEDER ? IF YES PLEASE ADVISED WITH CODE ARTICLE

Status
Not open for further replies.

loco79

Member
Location
miami
Occupation
electrical inspector
ACCORDING TO 250.30 A IT DOSENT REQUIRED TO HAVE PULL A NEUTRAL TO BOND TO ANY OF NON CURRENT METAL PARTS OF THE F/P CONTROLLER
PLEASE ADVISED IF IT REQUIRES BY NEC

AND DONT HAVE ODJECTABLE CURRENT DUE A CONNECTION BETWEEN A NEUTRAL AND EQUIPMENT GROUNDING CONDUCTOR .
 
I see where you are going with that, but never seen one have nothing but a egc. Could say it’s a reduced neutral?
If it is service equipment, supplied by a grounded system, you are required to bring the grounded conductor to it. It would be sized per Table 250.102(C)(1).
 
Looks like he posted the original and hasn't been back..
 