Simple question on wording (2020 but I don't think it's changed much):
When exactly can you not use 3/8" FMC? Feeding subpanels or what isn't really "utilization equipment"?
What brings this up is I need to fish through a wall from a panel into a crawl space where I can switch to EMT. Is this okay or do I need to jump to 1/2" or use MC+jbox (which is also 3/8 and this is nanners if that's the case)?
So utilization equipment means... what exactly here? Only on the termination side? Anywhere in the run?348.20 Size.
A. Minimum. FMC less than metric designator 16 (trade size 1∕2) shall not be used unless permitted in 348.20(A)(1) through (A)(5) for metric designator 12 (trade size 3∕8).
- For enclosing the leads of motors as permitted in 430.245(B)
- In lengths not in excess of 1.8 m (6 ft) for any of the following uses:
- For utilization equipment
- As part of a listed assembly
- For tap connections to luminaires as permitted in 410.117(C)