Maybe a dumb question - a new ATS (3-pole) is being installed to switch a 3 wire generator feed and a 480V 1200 A utility feed with GFP. The service disconnect is upstream of the ATS, and N-G bond is at the service disconnect. The generator MCB is 1000A, also with GFP capabilities. Feeders from the service disconnect and from the generator are each 3-wire+G with no neutral pulled (no 277 VAC loads).
3-wire feeds should only require a 3-wire switch. Is there any scenario where i'd need to pull the neutral and install a 4-pole to ensure GFP at each breaker functions properly under all scenarios? I'm saying no, but am going around in circles a bit concerned I am missing something.