Yeah I agree, there would be no need to use the 'open phase' with the OP's loads.If you have transformer windings connected A-N-B and A-C, any single-phase load on C-B will flow through and load both transformers; not an optimal configuration. Similarly, a load on C-N will flow through A-C and A-N.
If we had a 37.5 lighting pot and a 25 power pot and put one of the 15.1 kilns across the open phase
then the lighting pot would reduce to 27.6 and the power pot to 13.8,
so using the open phase would cost ~6kva more than just using the power or lighting transformers.
I would just simply put a 15.1 kiln and the 9.7 kiln on the power pot and one 15.1 on the lighting pot then you'd have 22.4 kva left over for the rest of the loads.
I am sure that a open delta would cost less than a wye as its one less transformer to provide, mount, wire maintain etc.