At what point do you have to separate the line and the load conductors from being in the same conduit? I'm thinking in regards to service conductors and/or feeders.
For feeders or branch circuits they can be within the same raceway. For something like a circuit with a VFD the manufacturer might recommend that they not be within the same raceway.At what point do you have to separate the line and the load conductors from being in the same conduit? I'm thinking in regards to service conductors and/or feeders.
Seen a lot of VFDs withe line and load in the same pipe. Not supposed to be that way though.For feeders or branch circuits they can be within the same raceway. For something like a circuit with a VFD the manufacturer might recommend that they not be within the same raceway.
Permitted within service equipment just not in the same raceway.What about service equipment?
I was on the same page, until we found it.I've always thought the possibility of a conductor getting hot enough to melt through it's own insulation, not short out to the surrounding grounded raceway it may be contained in, melting through another conductor's insulation, making contact with that conductor, which would have to be the same phase of the conductor that melted in the first place, and go on to bypass the overload protection by doing so would be nothing short of a small miracle.
JAP>