Labored up 4/c #500 Vitalink MC cable that's 9,500 lbs per thousand feet. They are now using 1/C #500( which is more practical) and the weight of this is 2,600 lbs per thousand feet. So it's almost a 1/4 the weight of the 4/C. We don't have historical labor units for the 1/C but would you say the labor unit used for the 4/c should be reduced by at least half due to juist the weight reduction? Should it go in about 1/4 to 1/2 the time the 4/c would've taken? Thanks.