I am hoping to find a way to install two pieces of testing equipment with 200 kVA and 400 kVA peak loads at site with only a 750 kVA utility transformer, 350 kVA observed peak load over the last year, and a low load factor. The existing peak load is driven by supplemental resistance heating in winter. The test equipment is all PLC-controlled, and we can program it however we want. We're fine to throttle the test equipment occasionally to stay within the available service capacity.
I am confident that it is technically possible to build a controller that measures current on each phase and provides a dynamic power limit that the test equipment follows to stay within the 750 kVA service capacity. But I have no idea how to convince an electrical engineer that some custom, unlisted piece of equipment is going to keep us from burning up the transformer.
Is there some kind of controller that can monitor power usage and shed loads to stay within a limited service capacity? Ideally, it could communicate a power limit to the equipment and give the equipment a chance to comply, but if it simply disconnected circuits according to priority when a power limit was reached, that could work, too.
Surely, we can't be the first people trying to make the most of a limited service capacity with low load factor equipment. I know EV chargers sometimes have some similar capability, and there are a few residential smart load centers available. What products exist for commercial / industrial usage?