OK Sparky 93
- Iridea14Strat
- Electrician
I’m stretching here.
When it comes to Vd and wire size and distance, I want to play out a scenario. I don’t know actual distance, only guesstimating.
5HP motor 1 phase
21.9 nameplate amps
30.8 per table amps
Approximately 200ft
208 volt
Based on info #10 would only be good for about 115 feet.
There entire length would need #6. Another entity told customer they needed #8.
It currently has #10
The way I see it is at the least #6 would or could be installed to the point that the #10 could handle.
Does anyone see it differently? Would you see anyway #8 could be ran, unless the total distance is less than what I am estimating?
I don’t see the real need at this point to need to run #6 the entire distance. Just an intercept.
5HP motor 1 phase
21.9 nameplate amps
30.8 per table amps
Approximately 200ft
208 volt