Wanted to know if 2 ground rods would be required for a irrigation pedestal meter / combo. No ground resistance testing will probably be done.
correct, it is the HOA who pays all the way.I take it the pedestal is customer owned and the power company is not providing it?
JAP>
I think I answered it in the beginning. I would think that if it's a meter/main /combo it would be service. Maybe because I am used to the peoples republic of California.Is it supplied by a service or a feeder?
Service or feeder wouldn't change anything although I've heard that some locales allow a single rod with a separate structure for a feeder. NEC still requires two unless tested.I would think that if it's a meter/main /combo it would be service
Would an irrigation pedestal be a structure ??Service or feeder wouldn't change anything although I've heard that some locales allow a single rod with a separate structure for a feeder. NEC still requires two unless tested.
Good question, I missed the pedestal part and assumed it was a structure. You're correct that the service would require a GES, an irrigation pedestal just an EGC.Would an irrigation pedestal be a structure ??
How would it differ from a RV pedestal where most folks don't require rods.
(Assuming it's a feeder---- with the meter is likely service and rods are required....just covering bases )
NEC Definition:Would an irrigation pedestal be a structure ??
Two rods based on what? Is it fed by a feeder or a branch circuit? Is it a structure?Irrigation pedestal here includes a 100 HP PP, pivot, and fertilizer equipment.
Two rods!!
It being a meter/disconnect it is safe to assume a service feeder.Two rods based on what? Is it fed by a feeder or a branch circuit? Is it a structure?
The discussion shifted to when the irrigation pedestal is NOT fed by a service as Augie mentioned in post #7. If it's not fed by a service then are ground rods required?It being a meter/disconnect it is safe to assume a service feeder.
No pictures, so is it or isn't it a structure based on NEC Definition? Most likely a structure, unless the meter/disconnect is somehow a free standing piece of equipment (Never saw one) it would be mounted to some sort of structure.
As a branch circuit, no. As a feeder, yes.If it's not fed by a service then are ground rods required?
Could also be a branch circuit?Back to the age old question of when is something a structure.
Here, we build something to hold the misc equipment. It is not free standing. Could be either a Service or Feeder.