130 feet of SER 4/0 Al. Have you run this long ?
Stevenfyeager
United States, Indiana
electrical contractor
130 feet of 4/0 SER Al from disconnect to 200 amp panel in house. I don't think I've installed a 200 amp residential panel that far from a meter disconnect before. Voltage drop on line calculator says 2.3 % drop. Does this sound ok ? Thanks.
Even at 200 amps you have less than 3% drop and as Larry says these loads are historically lower than the ampacity
It’s not hard just very labor intense. I hate that crap lol. Rather pipe it and pull if possible.
It really depends on the route. If you're able to pull through an attic or if it's going through a bunch of framing up and down through walls. Sometimes you need a bunch of people to help.
Rob G - Seattle
Rob G - Seattle
Good point!
it’s just me so I have to make it work lol.