kenaslan
- Billings MT
(2) Large Equipment.
For large equipment that contains overcurrent devices, switching devices, or control devices, there shall be one entrance to and egress from the required working space not less than 610 mm (24 in.) wide and 2.0 m (6 1⁄2 ft) high at each end of the working space...
My question here is what is the code intent of the word "Entrance"?
If you look at all the diagrams in the handbook, they seem to always indicate a door. 110.26(3) "Personnel Doors" require panic hardware if the door is within 25' of the clear space. This would reinforce my belief that the word "entrance" is a door, not just escaping to a clear area. If you have 7 or 8 rows of MCCs facing each other you need clearance at each end (unless you double the clear space 4 feet becomes 8 feet and don't forget to add the 24" between open doors) you can look to the left or right, and MUST see a door one way or another with a clear and unobstructed path.
Thoughts?
Thoughts?