winnie
- Springfield, MA, USA
- Electric motor research
That bare wire needs to go to the load side neutral terminal of the GFCI. If the cable is SE and from a main panel (not sub panel), that would be grandfathered legal and should work. ...Removing the jumper removes the safety bonding from the dryer frame, but the GFCI should save a person when being shocked by tripping.
Best solution is to install a proper 4 wire circuit. But that may be difficult and expensive. Or eliminate the GFCI and do it the old school way with a bonding jumper between neutral and the dryer frame.
I strongly with removing the frame bonding to use a GFCI. Now you would have a floating metal frame on an appliance that is supposed to be grounded/bonded, and are depending on the GFCI alone for shock protection.
I know that GFCI protection is permitted for ungrounded 120V circuits, but this would be creating an ungrounded circuit to use a GFCI.
Just install the 4 wire circuit and be done, or convince the AHJ to permit the non-GFCI circuit to remain.