- New Jersey
- Journeyman Electrician (retired)
It clearly states "will have an ampacity equivalent to that of the installed ungrounded supply conductors." The conductors installed are 1020 amps so that's the number you would use for the comparable conductors of another material, not the OCPD of 1000 amps.The only remaining question I have when applying Note 2 is whether it's fair game to say "the OCPD is 1000A, if I had used 3 sets of Cu they would have been 400 kcm, so that's the basis for comparison." Or whether you have to say "the ampacity installed is 1020A, to match that with 3 sets of Cu we'd need to use 500 kcm, so that's the basis for comparison." The former gives you a 3/0 Cu SBJ, the latter a 4/0 Cu SBJ.
Note 2. If the ungrounded supply conductors are larger than 1100 kcmil copper or 1750 kcmil aluminum and if the ungrounded supply conductors and the bonding jumper are of different materials (copper, aluminum, or copper-clad aluminum), the minimum size of the grounded conductor or bonding jumper shall be based on the assumed use of ungrounded supply conductors of the same material as the grounded conductor or bonding jumper and will have an ampacity equivalent to that of the installed ungrounded supply conductors.