Elect117
- California
- Engineer E.E. P.E.
That answer is illogical, interpreting the language in Note #2 with any consideration for the physics involved gives a minimum size of 3/0 Cu.
Cheers, Wayne
I wouldn't say illogical.
I am going to try to calculate the equivalency using their impedances (I am going to use aluminum conduit numbers and hope that is the worst case, highest impedance on the return path).
Aluminum 600kcmil-
wire 1 // wire 2 // wire 3 -> 0.041+j0.039 // ... //... -> 0.01367+j0.013 / 1000 ft (0.01886<43.57°)
12.5% -> 1/.125= a kcmil reduction factor of 8. so the impedance should be acceptable to increase by the same factor.
8*(0.041+j0.039) = 0.1093+0.104i/1000 ft (0.151<43.57°)
closest aluminum conductor with the same or less impedance is 250kcmil Al (0.090+j0.41) (but depending on the rounding made by table 9, maybe 4/0 Al).
closest copper conductor with the same or less impedance is 2/0 (0.10+j0.043).
You could convert the parallel impedance of the ungrounded conductors and multiply by the 12.5% factor (8x) and get 2/0 copper as okay.
I just don't know if it is correct to assume that the SBJ, SSBJ, MBJ's purpose is a low impedance bond or if there are other considerations that I missed.
But if someone told me I had to choose one for a plan set that was due today, I would go with 4/0 and be done with it. It is just a small piece on a transformer anyway. We aren't talking about running this for hundreds of feet. If someone installed 3/0, I wouldn't loose sleep over it either. I probably wouldn't loose sleep over 2/0 either to be honest.