JovialBulge
 - New England
 - Automation Dude
Device is UL listed as explosion proof for CID2 and requires 24VDC @ 250mA to operate. I assume I can install this device within a CID2 location based on this information and referencing this section of the code.
500.7(A) Explosionproof equipment
500.7(F) Nonincendive circuit
I must use flexible wiring to this device based on its location within the overall machine so I assume that has to be done in accordance with the hazardous location. Which brings me here in the code.
501.10(A)(1)
501.10(B)(2)(1)-(7)
Specifically 501.10(B)(6)Flexible cord listed for extra-hard usage and terminated with listed fittings. A conductor for use as an equipment grounding conductor shall be included in the flexible cord.
501.140(A)(2)
I then meander to Article 400 and more specifically Table 400.4 to determine which cables are considered to be "extra-hard" usage.
So long as the cord is correct for the location based on the referenced table above (400.4) and it’s terminated at both ends correctly; one side will be into the device itself which has a female NPT port and then into UL listed type 4 or 4X enclosure. Is there anything else that I need to consider with this installation?