TwoBlocked
- Bradford County, PA
- Industrial Electrician
I think I have this figured out, but would like input from you fine folks. All Code references are from the 2023 NEC.
When the NEC mentions an explosionproof enclosure, I picture one of those cast aluminum bolted boxes with breakers or contactors in it. But a measuring device such as pressure transmitter that is listed as explosionproof would also be such an enclosure, right? So when running conduit in a Class I Div 2 area to such a measuring device, the conduit must be sealed as per 501.15 (B) (1) (which further references Class I Div 1 wiring methods). So before the seal, Class I Div 2 wiring methods are allowed such as listed LFMC and condulets with gasketed covers, but between the seal and the explosionproof measuring device Class I Div 1 wiring methods are required such as capped elbows and explosionproof unions, right? Of course a boundary seal will probably be required when transitioning to an unclassified area.
Am I missing anything?