Hello quick practical question for you all that have experience installing meters,
For a plug-in type ANSI C12 Form 2S Class 200 meter (typical 200A meter for Form 2S meter sockets in North America) how does the meter itself get grounded? For most meters, I see a horizontal busbar/grounding terminal on the back of the meter at the midline. For ringless meter sockets, I typically see rings (see picture) or terminals around the left and right sides such that the meter's grounding terminal would contact this when inserted. However, for a ring type meter sockets (see example) they don't have these internal grounding rings and the meter's grounding terminal (aka surge relief gap?) looks like it makes contact with the ringed panel (which is painted) rather than any grounding terminal inside the meter socket. ANSI C12.7 does specify that "in sockets of all types, means shall be provided for grounding the surge relief gaps of the watthour meter" so they must have a grounding means, but not sure if that would just be a grounding screw or if the intention is one takes off paint at the appropriate location on the ringed cover or something.
Can anyone shed light on how a Form 2S meter is intended to be grounded when installed in a ring type meter socket?