AlbertL57
- Falls Church, VA
- Solar maintainer
No supplier seems to stock them, and they're quoting lead times of 6 months or more. Does anyone know what happened to that supply chain?
Thanks for postingSee-for instance: URL
No.Are those allowed to reduce AFC to cheaper equipment ?
I'm mystified. How are these different from a fuse or circuit breaker? The spec sheet appears to only deal with wire size, and doesn't mention current... How does it -know- it's time to open the circuit?
Yes, it does seem mysterious! You're correct - they are rated only by wire size and material (e.g. 250MCM Cu). Internally, they must have some kind of fuse element, apparently rated only on the basis of preventing the wire or insulation from melting.I'm mystified. How are these different from a fuse or circuit breaker? The spec sheet appears to only deal with wire size, and doesn't mention current... How does it -know- it's time to open the circuit?
Here's a similar service from Pepco in Washington, DC. Yes - in their world, green is a phase color!These are what ConEd specified. A little sloppy IMO but this was installed by their sub-contractor.
That's pretty much what it isIt sounds like a large fusible link.
Which open after the conductor has already faulted, hopefully preventing/reducing damage to the other conductors in the set. It may be better to limp along on a reduced number of parallel conductors than it is to lose the entire facility while waiting for new conductors.It sounds like a large fusible link.
Wonder what tool was used on those crimp lugs?These are what ConEd specified. A little sloppy IMO but this was installed by their sub-contractor.
The paperwork says they don’t offer over current protection, just short circuit. Personally never even heard of the things, let alone installed them.I'm mystified. How are these different from a fuse or circuit breaker? The spec sheet appears to only deal with wire size, and doesn't mention current... How does it -know- it's time to open the circuit?
A poor moron was used.Wonder what tool was used on those crimp lugs?
I believe that the ConEd spec calls for an indenter type of crimp.Wonder what tool was used on those crimp lugs?
I believe a lot of their use is on the utility side, specifically on secondary networks (multiple transformers paralleled on the LV side, usually underground) where available fault currents are very high. By quickly isolating individual faulted cables, the limiters help maintain service continuity.The paperwork says they don’t offer over current protection, just short circuit. Personally never even heard of the things, let alone installed them.
How does thus compare to a typical OCPD? Your example is for a limiter to protect 500kcmil which is typically applied at roughly 380A. The TCC shows this limiter would carry roughly 2500A for10 sec before opening. This doesn't seem like it would be easy to coordinate with.Bussman makes them. Not sure why the long lead time. It's essentially a current-limiting fuse. Here's a TCC for 500 kcmil Buss limiter (according to EasyPower).