This is a TIA that was issued before the first edition of the 2023 was published, so it was automatically adopted when the 2023 code was adopted.gException No. 2:
GFCI protection shall not be required for listed HVAC equipment. This exception shall expire September 1, 2026.
What makes you say that? Don's information in post #6 is not in agreement, and Exception #2 to 210.8(F) still shows up in the 2023 NEC on nfpa.org/70.As I understand it ... GFCI are back on and required everywhere for the 2023 NEC. All TIA (Temporary Interim Amendment) have expired or have been denied.
While the SPGFCI may solve the problem, they are not readily available as as far as I know there are no plans to have a breaker type SPGFCI. They are all large, and expensive stand alone devices, and they require an additional conductor between the SPGFCI device and the protected load. This is used to verify that the EGC is intact. If either the EGC or the "ground check" conductor is open, the device will open the power circuit.Effective September 1, 2026, GFCI or SPGFCI protection shall be provided for listed HVAC equipment.
Solutions to problems that never existedI don't think the issues will be resolved by the 9/1/26 expiration date, but the first draft of the 2026 code says.