See 240.4 (B) There are 3 conditions and ALL must be met.Can #1copper be used with 150a breaker being same size up from 125a per nec 240. The feeder is under the 800a
Are you saying that in the scenario outlined in the OP they are not met or are you providing the actual code reference?See 240.4 (B) There are 3 conditions and ALL must be met.
For adjustable trip. Is it saying it needs to have one or not ? I'm not clear on the condition.See 240.4 (B) There are 3 conditions and ALL must be met.
No adjustable trip is not required.For adjustable trip. Is it saying it needs to have one or not ? I'm not clear on the condition.
Not insinuating anything sir. Just providing the NEC reference.Are you saying that in the scenario outlined in the OP they are not met or are you providing the actual code reference?
Just checking, in thought that maybe I gave him the incorrect answer.Not insinuating anything sir. Just providing the NEC reference.
If you had, what would that make your lifetime total, two ???Just checking, in thought that maybe I gave him the incorrect answer.![]()
I know that it's been more than that but that's why I have all of you guys to correct me.If you had, what would that make your lifetime total, two ???![]()
I've had at least two!If you had, what would that make your lifetime total, two ???![]()
Today !I've had at least two!![]()
Make no mistake, I keep track of ALL the mistakes moderators post on line!I know that it's been more than that but that's why I have all of you guys to correct me.![]()