victor.cherkashi
- NYC, NY
I need to supply power to a roof-mounted 5-ton Mitsubishi condenser unit, which includes one compressor with a FLA of 19A and two fans, each with FLA of 0.8A. The unit operates at 208/230V, single-phase, MCA = 40A and MOP = 45A. I was curious why the MCA is 200% of the FLA, so I reached out to technical support for clarification.
Mitsubishi's support explained that the compressor current listed in the specifications is based on standard operation at 230V. For operation at 208V, you should add 20% to the FLA. In extreme weather conditions (0°F for heating or 115°F for cooling), the current can increase by another 40%, which is why the MCA is set at 40A.
Since the building's system is 208V three-phase, I need to account for 34.6A per unit, calculated as (19 + 0.8 + 0.8) * 1.2 * 1.4 = 34.6A. Multiple units like these connected to the same panel will significantly increase the size of the feeder and panel.
This is the first time I've seen such a large discrepancy between MCA and FLA.
WHO gave them an idea for the exclusion of the 40% current increase from the FLA for extreme weather conditions.? What if 115°F temperatures last for 5 hours or more?
I would appreciate your thoughts on this matter.