Depends where the receptacle is, years ago when I first got hit by 250.114 it was when I changed a 2-prong receptacle to a 'no equipment ground' GFCI at a built in computer desk aka "information technology equipment".
The second time it was old kitchen 'reface' that had a counter top & back splash being updated, I tried the 'no equipment ground' inspector thought 250.114 applied because your likely to use "Hand-held motor-operated tools" on a kitchen counter top and the fridge.
Pulling the old metal boxes would have disturbed the new tile so I did 250.130(C)
Anything outdoors is also a no-go