Dvelasco626
- Los Angeles
- Electrician
Do I need to ground the main water line if there is a UFER ground already in place? I am in California
IMHO... You are not grounding the main water line. Its already grounded.Do I need to ground the main water line if there is a UFER ground already in place? I am in California
Nor is bonding to the metallic internal water supply.If a metal buried water pipe qualifies as an electrode then it must be used as part of the grounding electrode system (GES). It is not optional even with a CEE.
That's correct, and note kwired's the use of the word system. It the water piping system is not all metallic it does not require bonding.Also as mentioned if you have metallic water piping system but not a water pipe electrode, you still need to bond the water piping system per 250.104(A)
Though there has been some debate on here before on how much of the system needs to be metallic to be called a metallic system.That's correct, and note kwired's the use of the word system. It the water piping system is not all metallic it does not require bonding.
Basically... Yes.Do I need to ground the main water line if there is a UFER ground already in place? I am in California