Detached building sub panel replacement
Dsg319
West Virginia
Wv Master “lectrician”
Replacing a Main lug only sub panel in a garage.
#2awg aluminum is existing. Hoping the feeder is on a 90amp breaker as it’s already existing.
Customer wants a main breaker in garage for ease of adding stuff and working in panel.
I plan to just use a sub panel with a 100amp main as that is a standard size in the big box stores with the amount of spaces I need.
To keep from a fused or knife switch disconnect or other methods is anybody else seen #2awg aluminum feeding a 100amp subpanel if the feeders protected at 90amps.
I know the conductors are properly protected with the feeder breaker but just wondering if this is the norm for this scenario.
You can feed a 600a MB sub-panel with a properly-protected feeder of any size adequate for the load. So, yes, it's okay.
The sub-panel's oversized main breaker is effectively rendered a switch (but could theoretically trip first with a bolted fault)
I am just wondering if anyone sees this done very much. Seems about the cheapest route to go.
If you want to feed a 100 amp panel with a 100 breaker my understanding is your feeder would have to go to 1/0 Aluminum.
There is nothing wrong with feeding a 100 amp breaker with 2 Aluminum fed by a 90 amp breaker. Wire is protected to its rating.
2-2-2-4 Al mobile home feeder is advertised as 100A. It is if it's for the main panel in a dwelling. But if going to a subpanel, you have to use the table, which says #2 is 90A. With that said, I do it all the time for a sub. It's the cheapest way to feed a sub. I use a 90A breaker. Most won't even come close to pulling 90A so it is fine. I also use a main breaker panel since that's the easiest way to comply with the remote building needing a disconnect.
Seems to be the case more often than not in detached building subs around here. The 100A sub in my detached garage is fed by an 85A feeder.
I don't think I've seen a single instance (other than mine) where the wire size increased or breaker reduced for a 100A sub feed panel. Almost to a 100 % will find #2 and 100A feeder breaker.
Most work in this area is being done by non-electricians, and for a subpanel will almost never get an inspection, and they simply go to big box or supply house ask for 100A wire and given a #2 AL. Around here even supply house if you want a a minimum size #1AL or even 1/0 it's not available or would be a 6-8 week order time. 2/0 is a little more available but not what the store will cut them when they ask for a 100A wire.
Really that long, WOW. I put a sub-panel in my garage and ran #1/0 SER which I picked up the same day at my local supply house. Around here if you want to waste money and skip the supply house Home Depot will deliver it in a few days.
Why would your local supply even stock #2 SER and not #1?