Commercial 480V inverter with PCS

Status
Not open for further replies.

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
Does anyone have experience with or know of a commercial inverter with PCS control that I should look at for a site with 480Y 3ph service? Need approx 125kW of inverter capacity. Would like to land it on a 200A backfed breaker in an 800A Eaton panelboard, and avoid downsizing the main breaker. 2023 NEC.
 
Does anyone have experience with or know of a commercial inverter with PCS control that I should look at for a site with 480Y 3ph service? Need approx 125kW of inverter capacity. Would like to land it on a 200A backfed breaker in an 800A Eaton panelboard, and avoid downsizing the main breaker. 2023 NEC.
You probably know that you will have to find one with less than 128A of maximum output current.
 
You probably know that you will have to find one with less than 128A of maximum output current.
That is why I'm looking for one that supports PCS to not be restricted by 120%, using EMS/PCS per 705.13. I am already at 147% oversizing with a 120kW inverter and 176kW array, and can't really downsize inverter and achieve desired production.
 
Status
Not open for further replies.
Top