PluggedIn66
New User
- Sarasota, FL
- Electrical Contractor
Hello everyone, long time reader and first time poster here.
We are working on an upcoming project, where golf course is upgrading pump station for course irrigation. The pump station is prefabricated and UL listed with 405FLA stamped on nameplate). Pump station is 3PH 480V. The prefabbed station has a 600A fusible main disco built-in (with 600A dual element, RK5 fuses) , and we will also be installing a service entrance rated 600A fusible disco/manual transfer switch ahead of the pump station.. There is an existing 3PH 480V 400A service, fed with parallel 4/0 AWG THWN-2 Cu feeders in (1) 3" PVC conduit feeding previous pump station. Existing self contained meter can is 400/320A rated.
QUESTION: Can I replace the 400/320A meter can with a 600/480A can, and RE-USE the existing feeders? According to my calcs (and using the 90*C column for derating purposes), these parallel feeders are rated for a max of 416A (260A+260A*0.8), which is above the 405A FLA.
The prefabbed equipment with 600A disconnect is making me question whether we need to provide a true 600A to equipment. Other issues throwing me off (which may be a moot point due to UL listing of equipment?)...The pump station contains (4) 75HP motors, (1) 30HP motor, and (1) 5HP motor, all at 480V. My FLA calcs are higher than what is listed (96Ax4 + 40A + 7.6A), or 431.6A. At this point, the existing service feeders would not be adequate.
These pump stations are state of the art for the market, and contain VFD's for all motors...so maybe that is where they are able to decrease the FLA calcs...not sure on this one, or that it even matters.