- Chapel Hill, NC
- Retired Electrical Contractor
Someone called me and said they used a 60 amp breaker on a hot tub with 6/3 nm. The inspector turned him down so he showed them 240.4(B) and passed. I told him that if the load of the tub was 48 amps then the calculated load would be 48 x 1.25 = 60 amps thus 6/3 nm @ 60C would not work.
Then I started to think.... If we had 2 motors we would calculate one motor at 125% and then use the others at 100%. So why can't we use the larger loads of the hot tub (motor or heater) and just use 125% of the larger and then add the smaller load.
I believe this section does not allow it. Do you all agree with me? If so does anyone know why you can't use the smaller load at 100%.
430.24 Several Motors or a Motor(s) and Other Load(s).
Conductors supplying several motors, or a motor(s) and other load(s), shall have an ampacity not less than the sum of each of the following:
- (1)
125 percent of the full-load current rating of the highest rated motor, as determined by 430.6(A)- (2)
Sum of the full-load current ratings of all the other motors in the group, as determined by 430.6(A)- (3)
100 percent of the noncontinuous non-motor load- (4)
125 percent of the continuous non-motor load.