Alwayslearningelec
- NJ
- Estimator
This is only a part of a spec. I do not know what the NEMA 250 means.Came across this in my disconnect switch sppec section. So obviously that would mean the enclosure more than likely would have a female threaded hub?
That is the ANSI standard for enclosure types. However the certification to the NEMA standard is a self certification, like with a CE certification. If the product is required to be listed it would have to be certified by a NRTL.This is only a part of a spec. I do not know what the NEMA 250 means.
They want you to order enclosures without factory knockouts. There is nothing in that spec preventing you from making holes for conduit entrances in the field unless the enclosure is a type 7 or 9. There is nothing that requires you to use hubs unless they are needed to maintain the Type rating.
This is a pretty useless spec as Type 12 enclosure are the only ones, in this list, that are available with factory knockouts.
We typically sent them out to a machine shop to be drilled and tapped, but you have to look at the instructions as they tell you the sizes and locations where you can tap an explosionproof enclosure. That is the cases were we could not get one with factory holes to match our installation. The best it to use one with factory holes even if you have to close any extra holes with explosionproof plugs.As a practical matter you can cut knockouts in normal enclosures, but explosion proof enclosures have to be drilled and tapped and it is not something you want to do in the field.
Yes just about all the panels and disconnects are nema 4X. Why?Sounds like threaded hubs but are you using many of the Type 4, 4X, and 12 enclosures.
Thanks. You wouldn't tap a standard steel enclosure correct? Would imagine you need some thickness.Drill a hole with a drill bit, then use a tap to create threads.
View attachment 2573943 View attachment 2573944
Explosion proof enclosures are typically quite thick 3/8 inch or maybe half inch. The conduit fittings actually screw into threaded holes made in the walls of the XP enclosure. XP pushbuttons and lights screw into drilled and tapped holes too.Thanks. You wouldn't tap a standard steel enclosure correct? Would imagine you need some thickness.
The theoretical minimal thickness is 1/16", of which a 10-32 screw just engages two full threads.Thanks. You wouldn't tap a standard steel enclosure correct? Would imagine you need some thickness.
A lot of enclosures have tapped holes in them. Panel boards have tapped holes for ground bars and the bonding jumper between the neutral bus and the panel steel. Along with all the mounting holes.Thanks. You wouldn't tap a standard steel enclosure correct? Would imagine you need some thickness.
Assuming that the enclosures are not explosionproof, you simply drill or punch your own holes in the enclosure. I always specified no factory knockouts as that makes it easier to layout the conduit.So back to my original question. The panels and gear are NOT to have ko's. Agree? So then it would have to be a threaded hub. Agree?
Seems awfully unusual to have all the panels etc. have a threaded hub instead of ko.
Also applies to panelboards, gutters, & screw cover cans, also just makes the job easier.Assuming that the enclosures are not explosionproof, you simply drill or punch your own holes in the enclosure. I always specified no factory knockouts as that makes it easier to layout the conduit.
Drill then tap for a threaded opening your saying? So it would be a female internal threded hole so to speak?Assuming that the enclosures are not explosionproof, you simply drill or punch your own holes in the enclosure. I always specified no factory knockouts as that makes it easier to layout the conduit.
No tap..just round hole made with a hole saw or a knock out punch. The conduit would install with two locknuts and a bushing in interior dry location.Drill then tap for a threaded opening your saying? So it would be a female internal threded hole so to speak?