In NYC we are stuck with 2008 NEC with amendments.
In the updated code 310.15(B)(2)(a) exception it says "Adjustment factors shall not apply to conductors in raceways
having a length not exceeding 600 mm (24 in.)."
However in the 2008 NEC it does not say that. It only gives the exception for nipples and not raceways specifically: "Exception No. 3: Derating factors shall not apply to conductors in nipples having a length not exceeding 600 mm (24 in.)."
If I'm under the 2008 NEC, does this mean I still have to derate wires that are less than 24 inches in the raceway?