blueheels2
- Raleigh, NC
- Electrical contractor
Hey I’ve got a multi family service, 4 200 amp meter/mains over 1 wireway. Largest ungrounded conductor to each is 4/0 so I size the the gec to the metal water pipe off of the kill area of the 4/0 x 4 wires to get the size. 4/0 is 211,600, so 211,600 x 4 = 846,400 KC mil.
In 250.66 if I use AL wire the size would be 4/0 correct.
That’s the first question. If I’m wrong can you lead me to the right answer.
Second question. The water lines are 1/2 or 3/4 inch copper. Do they make a water bond clamp for that small of a pipe that will accept 4/0 wire. I’m not finding it. I don’t think split bolting to the 4/0 and reducing at each pipe to a wire size they would accept would be correct?
Thanks
Thanks