Johnny B.
- Sandy Utah
- Electrical Engineer 1
Hello all!
I need help on whether lights are needed in utility closets. Inspector is asking us to verify if we need lights in the water heater closets. I have water heaters for each unit with the access to them being in the corridor - instead of through the unit. My thinking is that the lights in the corridor should be sufficient - but NEC 210.70(C) says "(C) All Occupancies. For attics and underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch or listed wall mounted control device shall be installed where these spaces are used for storage or contain equipment requiring servicing. A point of control shall be at each entry that permits access to the attic and underfloor space, utility room, or basement. Where a lighting outlet is installed for equipment requiring service, the lighting outlet shall be installed at or near the equipment."
So my thoughts are the water heater closets could be interpreted as utility rooms. Is there a definition some where of the difference between utility rooms and utility closets? IBC maybe? That is the only argument I think I could make with the inspector on this.