Electromatic
- Virginia
- Master Electrician
I have a pumping station whose pumps are not running smoothly. We think it's mostly a mechanical/plumbing issue, but while investigating, I found what I consider a significant voltage and current imbalance with a motor running. The motor is 25HP, and the system is a high-leg 240V.
With the motor running, I have:
AB 240V
BC 237V
AC 235V
A 51.5A
B 53.5A
C 44.0A
Oddly, I get similar results with both an old motor and a newly-installed one. Also, there is a backup generator with slightly better voltage balance (238, 238, 241), and running off it, the motor pulls 51A, 53A, 46A.
Is there something I should look for to correct this, or is this a good as can be expected?
TIA
AB 240V
BC 237V
AC 235V
A 51.5A
B 53.5A
C 44.0A
TIA