2 transformers Z
chris kennedy
Miami Fla.
60 yr old tool twisting electrician
I have 2 100kVa transformers I’m doing available fault current calc for.
240V delta system
I know I add the kVa’a together and I also need to add the Z’s together also correct?
Thanks
240V delta system
Thanks
You do not simply add the kVA of the two single phase transformers when they are connected in a three phase open delta configuration.
When the individual transformers are the same size, you take 86.6% of the sum of the two which is equal to taking 57.7% of the total of a closed delta.
I believe the impedance are simply added together (I am too lazy to look it up).
Are you talking about two 1ph units in open delta a la Jim's response, or two separate 3ph units?
And, if two 3ph units, are they each separately fed in parallel, or in a step-up/step-down setup?
I’m sorry
2 single phase units wired 240V open delta.
Then I would think you'd treat each one individually, as independent loads.
Or are you asking about the impedance of the secondaries as a 3ph source?
If so, then my instincts say that the higher impedance is the limiting factor.