I'd be inclined to look at the directions.If you have a single raceway with 120v as a "power in" and "power out" to a control board and back out to a motor, would you just run one neutral wire? I am having a brain meltdown on this one.
If the switch in question is the control, one should suffice, unless the neutral current is monitored.If you have a single raceway with 120v as a "power in" and "power out" to a control board and back out to a motor, would you just run one neutral wire? I am having a brain me
Yes. In this case, the second terminal is there for convenience. You need not even jumper them.The two neutral terminals on the controls are common.
Can I bring one neutral to the controls that serves as the "in" and the "out"?