And I had better luck through 3MBut they aren't. Hilti and Spec Seal are the best in my experience. Not to discount any others. Just I have had personal experience with both of these and they were as helpful as one could expect.
called them, they said i needed to submit an engineering judgment request for firestopping.Don't email call Hilti. 1-800-879-8000 I promise they won't disappoint.
To answer your question. because just like the code, it means what it says. In this case "any combination" is not one cable. Firestopping has become very precise in the last 20 years.
After seeing this I did a few minutes searching Specseal's systems. This isn't difinitive, but every system had a maximum 2/0 MC cable size. I speculate that UL has not done an assembly with larger cable. Due to that, you will need to do what Hilti said. It isn't that difficult and it usually takes about a week. It was a free service the last time I did it.called them, they said i needed to submit an engineering judgment request for firestopping.
I see, waiting on their reply right now.. Can you show me that 2/0 detail?After seeing this I did a few minutes searching Specseal's systems. This isn't difinitive, but every system had a maximum 2/0 MC cable size. I speculate that UL has not done an assembly with larger cable. Due to that, you will need to do what Hilti said. It isn't that difficult and it usually takes about a week. It was a free service the last time I did it.
I agree with you about calling them. Some people are just plain afraid of the telephone anymore, don't seem to remember how to use themDon't email call Hilti. 1-800-879-8000 I promise they won't disappoint.
Excellent! Glad it worked out for you. Happy Thanksgiving!I asked for engineering judgement and they gave me a custom firestop submittal detail. Happy with it.