junkhound
- Renton, WA
- EE, power electronics specialty
1950s GE panel in church parsonage. 30A tied handle bolt on breaker.
What I have never seen before is a GE breaker trip and one side not make internal contact without a few cyclings of hte handles. Hard to find these old GE breakers, left the one in place after getting a 240V output.
Am the guy pastor call when something goes bad. 1 year old Vevor cooktop, no heat. Yes, pastor did check breakers and flipped on an off a few times.
So, meter shows 120V each side at cooktop, but no 240 V, figure the 120 on one side is just capacitve coupling. I had installed the cooktop last year and knew the 10awg was continuous from the panel.
Old 30A GE breaker, tied handles, open up and no 240V although breaker not 'tripped". Meter on breaker, flip a few times and lo and behold, 240 does finally appear.
240V not at cooktop, but the 1 YO vevor glass top resistance cooktop is dead.
Replaced with standard hotpoint 4 burner cooktop I had in the shop. Have not yet tried to troubleshoot the Vevor for why it tripped the breaker and is now 'dead'.