- EC - retired
An AB 1500 I installed 25 years ago has lost its programming twice in the last month and appears to be associated with a rebar driven into one of the 480 volt Cu feeder conductors. Not a failure but a ground fault. It has been dry since the 1st of September with only two rains. Each program loss coincided with the rain. The rebar caused fault was found during the 2nd rain.
The extremely expensive second PLC battery installed a few years ago has good voltage.
Would a SPD installed on the 1KVA(?) secondary feeding the PLC and associated controls help?