210.8b8 2017 nec explains areas that require gfci protection. Warehouses are not mentioned anywhere unless the code is considering them "similiar" areas.
other than within 6 ft of a sink 210.8(B)(5)There is no requirement for GFCI protection in a warehouse.
Or if it were a wet location or happened to be outdoors, or at least in any portions where those characteristics apply.other than within 6 ft of a sink 210.8(B)(5)